[技术互助] Any input on Cutler-Hammer Starter?

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 12:56 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-3-26 14:14 编辑   r; R- ?2 N% X/ x1 N6 X- I9 t

7 \% L1 c- W" g1 O2 FTwo  cutler –hammer advantage  starters are  doing the same thing:6 H0 G, d1 ^6 x5 t- L+ k
After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again.
; I: G+ V' ?, u: |It is a cycle.
$ W2 S" W  Y7 F" `0 p1 e2 [7 i6 O' e! ^2 W
We isolate the network control and use the local start and stop only, the problem remains.
4 @3 E8 D7 B& p& p6 o3 c3 p9 QSwap one of the defective buckets with a good one, the new bucket works fine.0 j* f* _$ r! T9 Q+ d
The problem should be inside the bucket.
( b4 \; g: u+ U( j- Z, x2 Y2 [1 z/ f/ S0 Q- P" ]# v* V
When the problem happened, we observed that  the contactor has a pulling action but will not seal.
$ B" {3 o7 I# L! aUse a terminating screw divers to push in the contactor, it will not seal either.
& j: F" T* g4 D" Y) q- `3 \" _" _Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same.' O  |7 P( q; C- n
( Z7 X3 P) N# ^1 J5 [" ^: y8 r
The next thing we can think of  is the coil, we took the coil out to have a close look.- h$ X* \( C" Q) k
They  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.
+ b0 W1 M' i$ ~( ~2 }4 D$ i5 c It is getting better  this time, we have 7-8 times of running before it quit working. # s8 l# ]6 W3 d' g% R' T. V  l5 B
, C: c( K: @# ^, U1 f. U
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
5 Y- B9 f/ Q8 t: {; ~/ w6 e8 O* @5 t' B
Do you guys have any input on this issue?
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑
) d, [( r) X8 q  a5 O3 c. D7 f% ?+ u' ]! P1 [, Z2 Z6 i9 e
中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
老杨团队 追求完美
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.
) W5 B$ s# w" XSince your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行
+ u1 ^9 U0 y0 t& |6 j8 W) O也想到这一点,不过这是新装的设备。
$ G8 f+ O5 \, s) R) P2 Q/ R1 e检查过触点没问题。