" u5 i I% A ]Two cutler –hammer advantage starters are doing the same thing:
# e# u* s' Z- P) x After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
- Z' v9 F- j) uIt is a cycle.$ g- |+ \# v# v3 q
3 h( K8 o; D! T5 w2 w
We isolate the network control and use the local start and stop only, the problem remains.$ P; v- L$ `5 l3 V. r- X7 @
Swap one of the defective buckets with a good one, the new bucket works fine.
* X% }% R0 O" B& ~The problem should be inside the bucket.
s: I0 c0 |, |5 P' }6 E* A) B
. E$ L* y+ f# y3 a$ v1 oWhen the problem happened, we observed that the contactor has a pulling action but will not seal.
0 Z8 y* P$ v" Y. N( S( @5 TUse a terminating screw divers to push in the contactor, it will not seal either.0 Q# D: D" L, W! `) C5 ~
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.
% m1 Z3 Y: r* h- ^ e1 ^6 e/ `6 J
The next thing we can think of is the coil, we took the coil out to have a close look.% Q) D3 Z7 u1 t% Q F
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.
$ u, M; p" O8 o4 H It is getting better this time, we have 7-8 times of running before it quit working. , w; N0 V2 X7 n
9 j8 k" y) r9 A! IThe coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. ( I" L* m! V0 O5 d! X: [( m
" u) d: M* c$ W( S% }# Z0 _
Do you guys have any input on this issue? |
|