本帖最后由 td456 于 2010-3-26 14:14 编辑 r; R- ?2 N% X/ x1 N6 X- I9 t
7 \% L1 c- W" g1 O2 FTwo cutler –hammer advantage starters are doing the same thing:6 H0 G, d1 ^6 x5 t- L+ k
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
; I: G+ V' ?, u: |It is a cycle.
$ W2 S" W Y7 F" `0 p1 e2 [7 i6 O' e! ^2 W
We isolate the network control and use the local start and stop only, the problem remains.
4 @3 E8 D7 B& p& p6 o3 c3 p9 QSwap one of the defective buckets with a good one, the new bucket works fine.0 j* f* _$ r! T9 Q+ d
The problem should be inside the bucket.
( b4 \; g: u+ U( j- Z, x2 Y2 [1 z/ f/ S0 Q- P" ]# v* V
When the problem happened, we observed that the contactor has a pulling action but will not seal.
$ B" {3 o7 I# L! aUse a terminating screw divers to push in the contactor, it will not seal either.
& j: F" T* g4 D" Y) q- `3 \" _" _Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.' O |7 P( q; C- n
( Z7 X3 P) N# ^1 J5 [" ^: y8 r
The next thing we can think of is the coil, we took the coil out to have a close look.- h$ X* \( C" Q) k
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.
+ b0 W1 M' i$ ~( ~2 }4 D$ i5 c It is getting better this time, we have 7-8 times of running before it quit working. # s8 l# ]6 W3 d' g% R' T. V l5 B
, C: c( K: @# ^, U1 f. U
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
5 Y- B9 f/ Q8 t: {; ~/ w6 e8 O* @5 t' B
Do you guys have any input on this issue? |
|