埃德蒙顿华人社区-Edmonton China

 找回密码
 注册
查看: 3366|回复: 3

[技术互助] A Tip on changing 3 phase AC motor rotation

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 11:27 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-4-14 12:28 编辑
: u4 \& j" K. @9 s/ t4 \6 L0 e( o2 U% a3 {
We all know that if you want to change the rotation of a three  phase AC motor.9 a$ K) S1 G9 Z9 ^0 c. I! P
Just swap any of the two phase leads.; {) W" i# [; V0 N/ d, x3 t( x
But for VFD application you need to do the swap after the inverter.
- f3 W+ i  Y1 i& ]8 m2 W& VIf you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.
& M: p$ Q/ T; V; f: F/ }& j; l" a; D! I5 E
As the principal of the VFD works, bascially from AC to DC, then DC to AC.
' d# S& q5 I7 ]6 v; v8 c5 g* Z
$ A# \% `' c3 F0 U3 {& D5 C; h# |The phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.
3 S; K. D+ K3 I- w# P4 z1 s  Y/ b, J0 S- Y  O# u
The only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.
鲜花(0) 鸡蛋(0)
发表于 2010-7-4 00:19 | 显示全部楼层
老杨团队 追求完美
k vo0u8p["
您需要登录后才可以回帖 登录 | 注册

本版积分规则

联系我们|小黑屋|手机版|Archiver|埃德蒙顿中文网

GMT-7, 2026-6-24 03:38 , Processed in 0.138887 second(s), 17 queries , Gzip On, APC On.

Powered by Discuz! X3.4

Copyright © 2001-2021, Tencent Cloud.

快速回复 返回顶部 返回列表