9 l: o4 d% q j5 v7 ?1 h8 c7 B. n fTwo cutler –hammer advantage starters are doing the same thing:
1 l# }+ ~3 ~- i! w3 D After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
: p4 `& W' ~& t1 h5 _It is a cycle.( v6 X2 A& e2 O
' T9 b; H; L5 p5 YWe isolate the network control and use the local start and stop only, the problem remains.! \; T5 m- A$ X4 O
Swap one of the defective buckets with a good one, the new bucket works fine.% J4 b! o+ D) M3 Z E+ N
The problem should be inside the bucket.
p. y% y. W" I1 C% m) \" a) a x3 H. M5 [
When the problem happened, we observed that the contactor has a pulling action but will not seal.' [9 U! d) c/ y, C2 G
Use a terminating screw divers to push in the contactor, it will not seal either.
/ U8 f6 n, w9 z3 n4 QConfirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.1 q& }, @9 `# H4 c
) B a9 E8 z, E" Z0 t% f
The next thing we can think of is the coil, we took the coil out to have a close look.$ t: T6 w" }! m4 G, U9 N4 |! [
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.7 D5 q6 a" {; Y+ x0 j
It is getting better this time, we have 7-8 times of running before it quit working.
: O8 Q1 r$ ]+ F7 G0 g8 h; Z2 Q+ [; R& ~6 t2 n' z
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. 0 x9 v0 a* O2 p! e9 u
4 }6 h7 j' B" H3 t3 V8 x" O2 b5 BDo you guys have any input on this issue? |
|