[技术互助] Any input on Cutler-Hammer Starter?

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 12:56 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-3-26 14:14 编辑 1 B/ L  s0 r+ j) ^5 Y* g

/ X$ N- A& V1 H6 }1 pTwo  cutler –hammer advantage  starters are  doing the same thing:
; S# `. ?/ P* E+ p  J After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again.
( L" i& }# m, g+ HIt is a cycle.8 e4 t' c% u; |! x; e
4 m2 o- j) v2 w+ U' e& A% s7 T
We isolate the network control and use the local start and stop only, the problem remains.7 F1 z, h" r/ f) \7 k% f
Swap one of the defective buckets with a good one, the new bucket works fine.3 T1 y& W# ^' Y2 Q9 B! c; Z
The problem should be inside the bucket.  U/ ^4 X6 m; M
& z5 K( g7 G& D2 n6 r, D1 Q. V
When the problem happened, we observed that  the contactor has a pulling action but will not seal.) t# ?; H! Y; K/ @! ^* _  s
Use a terminating screw divers to push in the contactor, it will not seal either.
0 i/ Q" _6 ]0 G7 R; c' TConfirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same.
: g% x$ c# ]4 U1 ^/ f
7 C/ W" Z. k/ z1 ~" s1 IThe next thing we can think of  is the coil, we took the coil out to have a close look.) x$ C5 }# q0 V, V
They  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.
+ m. u) X  P. f1 E: i It is getting better  this time, we have 7-8 times of running before it quit working. ; f; W8 p( V$ {% e5 N1 ^
2 T# g. l/ ~2 W" V9 _2 d* _* R
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. " G& H# }. V8 Y

6 j  }; b5 K" G' T; q  l% BDo you guys have any input on this issue?
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑 + G& R1 L* i) T$ w0 h

3 i# R+ l- H, D4 I% c; n中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
老杨团队 追求完美
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.
3 A  e  _. n/ ~- m+ _2 {- ?2 qSince your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行
# Q1 F- t7 n: Y$ b4 G9 g* f也想到这一点,不过这是新装的设备。
$ q' J- P3 \+ q- P0 G: o! v检查过触点没问题。
您需要登录后才可以回帖 登录 | 注册