[技术互助] A Tip on changing 3 phase AC motor rotation

[复制链接]
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 11:27 | 显示全部楼层 |阅读模式
老杨团队,追求完美;客户至上,服务到位!
本帖最后由 td456 于 2010-4-14 12:28 编辑
1 v% F' R/ M$ o* i1 h+ U
. e5 N" A0 X4 LWe all know that if you want to change the rotation of a three  phase AC motor.& g/ \4 m/ z: s9 T! W# g3 U
Just swap any of the two phase leads.
# j+ J. t- k/ a% OBut for VFD application you need to do the swap after the inverter.
$ i& `3 ^8 b/ x3 d+ r; V5 qIf you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.& M. w2 i' B! n- v
* P8 q9 L" |7 w6 r; T2 K
As the principal of the VFD works, bascially from AC to DC, then DC to AC. ; Z9 f( S8 n+ V

. a- F# w  g" bThe phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.
8 [: h* ?+ y  j" C. F
- k' c  T$ j) W' \% w5 p9 Y7 N/ LThe only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.