Two cutler –hammer advantage starters are doing the same thing:! g% z: |5 I9 o$ w2 k
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again. . @2 Q1 ]7 ~( p# \% e/ K+ ]0 W- p
It is a cycle.
) w, X4 D8 f. ]: y& w: g' v
7 {9 l* \' n$ E7 tWe isolate the network control and use the local start and stop only, the problem remains.
" \( H' w; m; M! X% ]Swap one of the defective buckets with a good one, the new bucket works fine.
L' X" Y0 {6 @) z1 {The problem should be inside the bucket.! ~& V) u# j9 L' I# k+ a0 Z
0 l/ I2 y5 [8 \. I; G1 LWhen the problem happened, we observed that the contactor has a pulling action but will not seal.; z M0 i+ k8 f
Use a terminating screw divers to push in the contactor, it will not seal either." X9 Z, w5 ?, |. u6 c0 i3 k* q- ^
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.
2 u, g' {' z, ~7 Q! D6 E/ Q( G1 B3 t( c
The next thing we can think of is the coil, we took the coil out to have a close look.) y$ A; C# U8 z7 ?/ R6 U1 a- D
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.
0 i# B9 V7 U, u5 _: [ It is getting better this time, we have 7-8 times of running before it quit working. 3 R: P0 n% y) e. L+ o8 k
" ]3 z, }4 b! D: O' E3 B
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. " p- n' X+ Z1 v1 h7 e7 [: t
7 b7 r; E) Q- j; I
Do you guys have any input on this issue? |
|