Two cutler –hammer advantage starters are doing the same thing:
n, a' v9 L6 `$ k' i8 W After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
- o9 @ q4 [1 L' JIt is a cycle.$ n: Y$ R8 R$ _
/ f3 Z# I+ B5 y. k6 Y% x
We isolate the network control and use the local start and stop only, the problem remains.. b; f" H0 Z+ ~# Z e5 O$ W- k9 G
Swap one of the defective buckets with a good one, the new bucket works fine.2 R" [7 A* A( m
The problem should be inside the bucket.
2 [9 J/ l# N) q( {3 t- \! p
* \" f' Y: I0 t) cWhen the problem happened, we observed that the contactor has a pulling action but will not seal.
' M; t. W8 p: j! T! [! F/ V, VUse a terminating screw divers to push in the contactor, it will not seal either.' ?0 c: a3 B+ E5 M# w; m; E
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.7 M& f# [4 y4 n$ s
" p! {. p! z% O; F3 y# ^" N. b4 yThe next thing we can think of is the coil, we took the coil out to have a close look.6 A, L) D+ l) K6 s5 I2 f
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.
8 R! p$ h3 y$ X' D It is getting better this time, we have 7-8 times of running before it quit working.
4 I% m* Y' k) R5 B% F5 U! C/ i ^! y( G# M# t, G, T6 N
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. 2 ^8 W% a0 E! x9 B
" d1 ~6 m5 `9 Z) J9 F8 f; d
Do you guys have any input on this issue? |
|