Two cutler –hammer advantage starters are doing the same thing: K: _' ]" l6 p5 \0 w5 W( X% m
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again. $ c/ p* `2 Z, {5 X+ I0 {* ]! I( \
It is a cycle.. J, n3 E8 z5 p: z+ o
! A1 r' N o+ `% p/ {6 SWe isolate the network control and use the local start and stop only, the problem remains.
5 d2 h% X) a- @9 d0 l3 KSwap one of the defective buckets with a good one, the new bucket works fine.0 H& I1 n" o' Y8 ^% X; _
The problem should be inside the bucket.
2 B( z) w( z9 s3 \; W# g( a2 o! O( C6 i* n# Q$ U
When the problem happened, we observed that the contactor has a pulling action but will not seal.
( \, t$ G5 C2 {. |- b) r( MUse a terminating screw divers to push in the contactor, it will not seal either.! }' {( T1 i7 O$ G, w+ S
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.0 _8 k9 [3 g3 S
2 G& m8 D4 T G: iThe next thing we can think of is the coil, we took the coil out to have a close look./ U: ^4 M5 m! {; v- L
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.2 m. h* L% X P6 ?1 l2 T5 U
It is getting better this time, we have 7-8 times of running before it quit working.
5 E& i3 U1 s/ w" E
0 N' Q% M0 W: k' j( \The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
0 h+ ?; g n# p! J) O) X1 |) Z- D7 |/ M% l: Y" @, g6 `9 o1 \
Do you guys have any input on this issue? |
|