本帖最后由 td456 于 2010-3-26 14:14 编辑 4 y% p# }0 `; z. {+ B3 w8 m' m5 n
: J; o6 R+ c& z5 M; R5 STwo cutler –hammer advantage starters are doing the same thing:. B3 O2 ~9 B7 T l
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again. * y9 L8 g: x/ ?: b
It is a cycle.
0 }$ W# K! c7 F5 `; z
& p- c { u( }8 h+ X& M C' TWe isolate the network control and use the local start and stop only, the problem remains.) s$ y5 |' j: b& z$ C- \. \
Swap one of the defective buckets with a good one, the new bucket works fine.7 {7 d4 q9 a) k5 q
The problem should be inside the bucket.
) {% @+ Q" R) L; }% r, u# p/ y- V- D* ^" Z, W5 @
When the problem happened, we observed that the contactor has a pulling action but will not seal.
. J/ O% z; F# d* C/ I+ vUse a terminating screw divers to push in the contactor, it will not seal either.
* h- M2 ^1 ~0 d% pConfirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.$ N) ^4 I: T3 g3 d8 U5 t1 n
" }. M- [; t7 v8 VThe next thing we can think of is the coil, we took the coil out to have a close look.
' K/ p& J" o9 D- m1 @They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.# e3 {: X& z& t0 e9 b2 n8 P
It is getting better this time, we have 7-8 times of running before it quit working.
; {- f& U! m$ D' ^3 W5 i. B1 c8 [& b7 q6 e' ~$ k
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
) n9 @+ l9 x4 U. |5 Q' ^9 D0 a$ Z, G1 O3 Z5 E" S
Do you guys have any input on this issue? |
|